The RMP function is not supported in Studio 5000, leaving me at a standstill in finding a solution to convert it to a Studio 5000-compatible function for a +/- 10Vdc analog output signal. Any suggestions on how to proceed would be greatly appreciated.
To access the AOI Ramp UP/DN, simply search for it on the Rockwell Automation website. Visit www.rockwellautomation.com for more information.
I've faced a similar problem before with Studio 5000. What worked for me was using the SCP (Scale with Parameters) function. This can handle the signal conversion by scaling your analog signal range to the desired +/-10Vdc. With the SCP function, you can define your input and output ranges that match your needs. Remember, SCP does not have any form of ramping capabilities, so if you need a smooth transition between setpoint changes you'd have to implement a separate logic. Planning this out on paper first really helped me map the logic.
I had a similar situation in the past. With Studio 5000 not supporting the RMP function, you might need to use a different solution for your analog output signal conversion. Consider using a Proportional-Integral-Derivative (PID) algorithm or Pulse-Width-Modulation (PWM), both have been effective alternatives for me in such scenarios. It may take some time to get it configured exactly to your needs, but in the end, you might end up with a system dynamic that is even more compatible and efficient than using RMP, given the constraints of Studio 5000.
You could try using the CPT (Compute) or the SCP (Scale with Parameters) instruction instead. Either can be used to scale your I/O to whatever range you need, and both are supported in Studio 5000. It might take a bit of tweaking to get it exactly right, but it should at least get you moving in the right direction!
I would recommend opting for a conversion approach. One way to do this could be to utilize a Proportional Integral Derivative (PID) loop to essentially emulate the RMP function. This will allow you to maintain a degree of ramping up and down for the 10Vdc analog output signal. However, setting up the PID loop will require caution to avoid overshoot or oscillations. It could be fine-tuned in a test environment before transferring it to the actual application.
Have you considered using function blocks in Studio 5000, like the PID instruction, to mimic the RMP functionality? You could build a ramping effect by incrementally adjusting your output based on the elapsed time or input parameters. Another option might be to implement a simple timed loop that controls the output voltage step by step. It might not be as straightforward as the original RMP, but it can achieve similar results with a bit of tweaking. Let me know if you’d like to dive deeper into the specifics!
It sounds like you're in a bit of a bind! One workaround could be to utilize the existing scaling capabilities within Studio 5000 by creating a user-defined function block that replicates the RMP behavior—essentially translating your input signal into a scaled output within the acceptable range for your +/- 10Vdc analog signal. You can implement a PID controller or a simple ramp timer in your program to handle the output smoothly. If you haven't already, check the Rockwell Automation knowledge base or forums, as someone might have tackled this previously with specific examples. Good luck!
✅ Work Order Management
✅ Asset Tracking
✅ Preventive Maintenance
✅ Inspection Report
We have received your information. We will share Schedule Demo details on your Mail Id.
Answer: 1. What is the RMP function in RSLogix 500 used for? - The RMP function in RSLogix 500 is commonly used for controlling a +/- 10Vdc analog output signal for proportional valves.
Answer: - The RMP function is not supported in Studio 5000, which can pose a challenge when migrating from RSLogix 500 to Studio 5000 for proportional valve control.
Answer: - To convert the RSLogix 500 RMP function to a Studio 5000-compatible function for a +/- 10Vdc analog output signal, alternative approaches or logic solutions may need to be implemented.
Answer: - Seeking advice or tips from experienced users or automation experts on how to effectively convert the RMP function to Studio 5000 logic can be beneficial in overcoming this challenge.