Do industrial control panels need a 40 amp main breaker on the 24-volt side?

Question:

Many industrial control panels feature a main breaker on the 24-volt side of the power supply, which then supplies power to smaller breakers. For example, a 40 amp power supply may have a 40 amp breaker on the +24 side that feeds 20 amp breakers connected to 24-volt branch circuits. Is it required by code to have the 40 amp breaker in place? It may be possible to simply connect a bus to the top of a row of breakers fed from +24 and directly supply branch circuit breakers. This setup raises questions about the necessity of the 40 amp breaker as mandated by electrical codes.

Top Replies

Is it necessary to have a breaker solely dedicated to powering other breakers? This may seem redundant, especially for low voltage systems.

I had the same thought - it seems redundant. If the intention was to have a single switch to power everything down, a simple switch or disconnect would suffice. After reviewing my coding notes, I couldn't find any indication one way or the other. I personally don't think it is necessary. The code specifies breaker/protection based on factors like power draw and distance, with no mention of one protection device preceding another. In my experience with industrial panels, I have never encountered this setup, so I recommend verifying that the 40 amp breaker doesn't feed the 20 amp breakers in another sub panel or device. It is more common for me to come across panels with no breakers or with bypassed ones due to frequent tripping. Those in the industry for a while can confirm this. So, consider yourself fortunate in this situation.

I appreciate both of your contributions immensely!

A great method to avoid overloading a power supply without using a 40A breaker is by distributing the load among multiple 20A individual breakers. By connecting 10 20A breakers to a 40A power supply, you can distribute a total potential of 200A safely. Just like in a house panel, where the main breaker safeguards the power supply while the branch breakers protect the individual feeder conductors and devices. This setup ensures that the transformer and feeders are protected while effectively distributing power to outlets and devices throughout the home.

Robertmee suggested a risky method of overloading a power supply by using multiple 20A breakers instead of a 40A breaker. By connecting 10 20A breakers to a 40A power supply, you could potentially draw up to 200A from it. However, it is important to remember that the branch breakers are there to protect the individual feeder conductors, while the main breaker is there to safeguard the power supply as a whole. While this may work in theory, it's worth noting that most DC power supplies are self-limiting and may not be able to handle such high loads.

While I see where you're coming from, it's actually quite important to adhere to the mandated electrical codes. This is primarily because the 40 amp breaker serves as a safety measure that prevents overloading and potential fires. Even though it may seem redundant, it ensures that the smaller, 20 amp breakers do not draw more than the 40 amps that the power supply can handle. The absence of the 40 amp breaker could lead to an overdraw of current and potentially catastrophic results. So, it indeed is more about safety than about the need. I would advise against bypassing any such precautionary measures stipulated by the codes.

While I understand the rationale behind thought of bypassing the 40 amp breaker, from an electrical safety standpoint, it's indeed crucial. It is mandated by specific electrical codes, such as the National Electrical Code (NEC) in the United States. This breaker serves as the main protection device for the panel, providing an additional layer of safety before the branch circuit breakers. Despite its seeming redundancy, having this main breaker handle a potential issue first, can reduce the chance of multiple smaller breakers tripping simultaneously, which could lead to bigger issues. So, although it might be technically possible to connect your branches directly, following code and maintaining this integrity is generally the safer and more compliant bet.

While I'm not an expert in every electrical code, generally such codes focus on ensuring safety, and the main breaker serves an important role here. It provides a failure point so that issues like short circuits don't overload the entire system. Removing the 40 amp breaker could pose a serious hazard in case of an unexpected surge or system failure. The main breaker isn't just about directing power flow, but also about protection. You should definitely check the specifics of your local electrical code and potentially consult an electrician before altering your setup.

That's a great question! Whether you need that 40 amp main breaker on the 24-volt side often comes down to local code requirements and the overall design of your control panel. Typically, having a main breaker provides essential overcurrent protection and makes troubleshooting easier, but codes can vary widely. It’s always best to consult the National Electrical Code (NEC) as well as any local amendments to ensure compliance. Also, considering the safety aspect, a main breaker can help prevent cascading failures and protect your branch circuits more effectively.

It's a great topic to delve into! From what I understand, having that 40-amp breaker on the +24 side serves as a crucial overcurrent protection measure, which is often required by code to prevent overloads from affecting the entire system. While it might seem simpler to run a bus directly to the branch breakers, bypassing the main breaker can expose the system to unforeseen issues and eliminate that centralized point of protection. Always best to check your local electrical codes and consult with a qualified electrician to ensure safety and compliance!

More Replies β†’

Streamline Your Asset Management
See How Oxmaint Works!!

βœ…   Work Order Management

βœ…   Asset Tracking

βœ…   Preventive Maintenance

βœ…   Inspection Report

We have received your information. We will share Schedule Demo details on your Mail Id.

To add a comment, please sign in or register if you haven't already..   

Frequently Asked Questions (FAQ)

FAQ: Do industrial control panels require a 40 amp main breaker on the 24-volt side according to electrical codes?

Answer: The need for a 40 amp main breaker on the 24-volt side of industrial control panels is a common question. While it may seem necessary for safety and code compliance, there may be situations where alternatives can be considered.

FAQ: Can a bus directly supply branch circuit breakers without a 40 amp main breaker in industrial control panels?

Answer: The discussion around bypassing the 40 amp main breaker and directly connecting a bus to branch circuit breakers raises questions about the compliance with electrical codes and the overall safety of the setup.

FAQ: What are the implications of not having a 40 amp main breaker on the 24-volt side of industrial control panels?

Answer: Understanding the implications of omitting the 40 amp main breaker, including potential safety risks, code violations, and impact on the functionality and reliability of the control panel, is crucial for proper installation and operation.

Ready to Simplify Maintenance?

Join hundreds of satisfied customers who have transformed their maintenance processes.
Sign up today and start optimizing your workflow.

Request Demo  β†’