How to Calculate Full Load Amperage (FLA) for Single Phase Components on 3 Phase Service

Question:

How to calculate the Full Load Amperage (FLA) of single phase components when operating on a 3 phase service can be a common question. For instance, with a 480V/3PH service, consider a 3kW electric heater operating at 480V/3PH, and a 1KVA transformer at 480V/1PH. To determine the total panel FLA, you may need to use formulas such as (3000 / (480 * 1.73)) + (1000 / (480 * 1.73)) = 4.8. Another approach could be (3000 / (480 * 1.73)) + (1000 / 480) = 5.7. It's crucial to calculate the FLA accurately for proper electrical capacity planning.

Top Replies

The bottom equation in your formulas is accurate, while in the single-phase calculation at the top, the square root of three is unnecessary. To improve accuracy, power factor should be included in 3-phase load calculations. A common practice is to use a power factor of .9 (Watts / 480 x 1.73 x .9 = current).I hope this information is useful to you.

I appreciate your input. While my usual approach has always worked for me, I have recently been contemplating the possibility that I may be overlooking a critical element. Despite my efforts, I have yet to pinpoint what that might be. In relation to your follow-up query about the scenario with (3) single-phase 1KVA transformers evenly distributed across the 3 legs, it seems to me that dividing by sqrt(3) would result in a total Full Load Amps (FLA) of 3.6 instead of 6.25. Is my understanding correct in this context? Moreover, if there were only 2 transformers involved, I am struggling to articulate my question clearly. I am curious about when sqrt(3) becomes relevant in such situations. After dedicating numerous hours to research, I am still unable to grasp this concept fully. Could someone direct me to a relevant whitepaper, video, or resource that explains this in detail?

When connected to a two-phase transformer, the three-phase resistive load of 3000/480 * 1.73 will only be added to the two connected phases, requiring an additional 1000/480 * pf. The power factor (pf) of the transformer can vary, typically starting at 0.9 at full load. As with motors, the power factor will decrease as the load on the transformer decreases. This variability in power factor is important to consider when calculating the overall efficiency of the system.

When determining the 3-phase loads and calculating the load for a 110-volt transformer and possibly a 240-volt transformer for AC units, it is essential to consider all three phases. Additionally, accounting for the appropriate factor for 3-phase loads, such as a factor of 1.25 for motors, is crucial for an accurate calculation. To account for any oversight or additional requirements, be sure to add 30% to the total load. This is a brief response as I am currently on break. - James

I do appreciate your comprehensive approach in the explanation! However, it's worth noting that for single-phase components in a three-phase system, the 1.73 factor won't come into play, as it's unique to three-phase computation. In your case, the transformer should be calculated independently at (1000 / 480), without the 1.73 factor. This is vital so that your resulting FLA is accurately reflective of the system's real load, ensuring accurate capacity planning.

Great explanation on how to calculate the FLA. Just to emphasize, one point to remember is that the 1.73 in the formulas is a result of square root of 3 (approximate value), which is the factor that converts between line-to-line and line-to-neutral voltages in 3-phase systems. It's also important to differentiate between calculating the FLA for 3-phase and single phase components as you've shown. Depending on the scenario, the formula adjusts to fit the required calculation, which could significantly impact your load figures and future capacity planning.

I like your thorough breakdown here. I just want to emphasize that the first formula calculates FLA for both devices assuming they are both 3 phase, while the second formula correctly identifies the transformer as a single phase device. So, for a more accurate total panel FLA calculation, the second equation, (3000 / (480 * 1.73)) + (1000 / 480) = 5.7, should be used in this scenario. Proper load calculation is indeed critical to avoid overloading and potential electrical issues. This choice of formulas surely depends on the phase of your devices. Always important to double-check the specifications!

Great insights on calculating FLA! It's definitely important to understand how single-phase loads interact with a three-phase system. Just a quick noteβ€”when dealing with the transformer, make sure to also consider whether it's running close to its capacity or not, as that could affect your total load calculations. Accurately calculating FLA ensures you don't overload your circuits, which can lead to efficient operation and increased safety. Thanks for sharing those formulas!

More Replies β†’

Streamline Your Asset Management
See How Oxmaint Works!!

βœ…   Work Order Management

βœ…   Asset Tracking

βœ…   Preventive Maintenance

βœ…   Inspection Report

We have received your information. We will share Schedule Demo details on your Mail Id.

To add a comment, please sign in or register if you haven't already..   

Frequently Asked Questions (FAQ)

FAQ: FAQs:

Answer: 1. How do you calculate the Full Load Amperage (FLA) for single phase components on a 3 phase service? - To calculate FLA for single phase components on a 3 phase service, you can use formulas like (Power in Watts / (Voltage 1.73)) + (Power in VA / (Voltage 1.73)) or (Power in Watts / (Voltage 1.73)) + (Power in VA / Voltage).

FAQ: 2. Why is it important to accurately calculate the FLA for proper electrical capacity planning?

Answer: - Accurate calculation of FLA ensures that the electrical system is not overloaded, preventing potential issues like overheating and equipment damage. Proper capacity planning helps maintain system efficiency and safety.

FAQ: 3. Can you provide an example of calculating the total panel FLA using the given formulas?

Answer: - For example, with a 3kW electric heater and a 1KVA transformer operating at 480V/3PH, you can calculate the total panel FLA by plugging the values into the formulas mentioned in the discussion thread.