Question:

Hello, I am having difficulty clearing the emergency stop failure on my machine during start-up. Despite disengaging all the switches, the machine will not proceed past this point. I am seeing green lights at the inputs. How can I resolve this issue and safely start the machine?

Top Replies

After reviewing the safety channels, it seems that there may be an issue with the feedback circuit and/or the reset function. Do you have a wiring diagram for the relay? The feedback contacts (N.C.) and reset button (N.O.) should be connected in series between S33 and Y2. When all contactors are off and you press the reset button, there should be a direct connection between S33 and Y2. It's possible that the error could be caused by a stuck reset contact. As per the manual, the relay resets upon the falling edge of the reset input. For further details, you can refer to the manual available for download here: [Link to manual].

How can I verify if my device is working properly? Sometimes, it powers on perfectly after shutting off all power, but then starts acting up again after 1-2 weeks of functioning well.

When troubleshooting a reset issue, check the contactors KC0 and KC1 for any issues. These contactors have a normally closed (NC) contact wired in series between safety relay Y1 and the reset pushbutton, as shown in the diagram. To determine if one of the contactors is the culprit, use a meter to test the resistance from Y2 to terminal 32 of KC0. If there is an open circuit, try probing Y2 to KC1 terminal 31. The goal is to find a closed circuit from Y2 to terminal 14 of the reset pushbutton, ensuring that pushing the reset button completes the circuit to S33 of the safety relay. If a contactor is found to be malfunctioning, it should be replaced promptly. It is worth noting that there are 3 contactors controlled by the e-stop relay: KC0, KC0/1, and KC1, with monitoring focused on KC0 and KC1. Further examination of the drawings may provide insight into why KC0/1 is not being monitored. These electrical issues can be tricky to pinpoint, but thorough troubleshooting is essential for resolving them.

If your ESR relay is constantly resetting with all lights showing green, it may be due to a dry joint on the contacts. This issue could indicate that the ESR is functioning properly, but there may be a faulty joint within the relay or a burnt contact. Another possibility is a fault in the cabling leading to the PLC. I have encountered several ESRs with problematic joints on the relays, leading to similar issues.

Thank you for your help! I'm struggling to find local assistance with emergency stop drawings. As a novice in this field, I am facing challenges but staying hopeful. The ESTOP concept is particularly challenging to grasp.

Hi there, it sounds like you've taken the right steps in troubleshooting. However, the issue might be a problem with the internal PLC or the software. Try rebooting the machine and see if the problem persists. Also, double-check your wiring and whether all safety protocols are correctly followed. IF the issue continues, you may need to call a technician or seek professional help.

It sounds frustrating to be stuck at that startup stage! Since you're seeing green lights at the inputs, it suggests that the system thinks everything is normal, but there might be a hidden fault or failure in the safety circuit. I’d recommend checking if there are any additional safety interlocks or reset buttons that might not be immediately obvious, as some machines have a secondary emergency stop that needs to be reset. Also, if your machine has an error log or diagnostic tool, reviewing that could provide some insight into what's causing the hold-up. Good luck, and stay safe while you troubleshoot!

More Replies →

Streamline Your Asset Management
See How Oxmaint Works!!

āœ…   Work Order Management

āœ…   Asset Tracking

āœ…   Preventive Maintenance

āœ…   Inspection Report

We have received your information. We will share Schedule Demo details on your Mail Id.

To add a comment, please sign in or register if you haven't already..   

Frequently Asked Questions (FAQ)

FAQ: 1. How can I clear an emergency stop failure on my machine during start-up?

Answer: To clear an emergency stop failure during start-up, ensure all switches are disengaged and check the input lights for any abnormalities.

FAQ: 2. What should I do if the machine does not proceed past the emergency stop failure point despite disengaging all switches?

Answer: If the machine does not proceed past the emergency stop failure point, troubleshoot the system to identify any potential faults or malfunctions.

FAQ: 3. How can I safely start the machine after resolving the emergency stop failure issue?

Answer: After resolving the emergency stop failure issue, follow the appropriate start-up procedures outlined in the machine's manual to safely initiate operation.

FAQ: 4. What should I do if I encounter green lights at the inputs during the emergency stop failure situation?

Answer: If you see green lights at the inputs during an emergency stop failure, consult the machine's documentation or seek assistance from a qualified technician to diagnose the issue.