Hello, I am looking to utilize the P_Intlk function and transmit the Status interlock OK bit to a P_DOut block. However, there are a total of 17 interlocks assigned to this output. Is there a way to utilize P_Intlk without using up an additional interlock? I also require access to all interlocks in a FactoryTalk View SE faceplate. Thank you in advance for your assistance.
To optimize performance, connect the output of one block to the 16th input of the subsequent block in a cascading fashion. This method enhances efficiency and overall system functionality.
Increase the quantity of one input and ensure that the text string in the Cfg_ConditionText accurately conveys the presence of two destructive bits associated with that particular input displayed on the faceplate.
Which library version should I use? While I don't recall ever needing it before, I do remember coming across a feature where interlocks can be accessed from graphics automatically. However, it is important to keep track of the naming of the Intlk block, as the animations rely on it for generation.
Certainly, you can definitely utilize P_Intlk without using up an additional interlock. My suggestion would be to use something like a P_Mux block. It will allow you to assign your 17 interlocks to each of its inputs while utilizing just one single output. This output can then be connected to your P_DOut block. As for accessing all interlocks in the FactoryTalk View SE faceplate, you should be able to accomplish this by creating an HMI faceplate for the P_Mux block, which displays the status of each interlock. Hope this helps!
It sounds like youβre in a bit of a tight spot with your interlock assignments! One option you might consider is using a bitwise operation or a logical OR function to combine the status of your interlocks into a single interlock bit. This way, you could potentially consolidate multiple interlock statuses without consuming additional interlock resources. Then, you can pass the combined bit to your P_DOut block, keeping the overall count in check. Just make sure to configure your FactoryTalk View SE faceplate to interpret the combined status correctly. Hope this helps!
β Work Order Management
β Asset Tracking
β Preventive Maintenance
β Inspection Report
We have received your information. We will share Schedule Demo details on your Mail Id.
Answer: 1. Can I use the P_Intlk function with multiple interlocks in PlantPax 3.2 without assigning additional interlocks? - No, each interlock used with the P_Intlk function in PlantPax 3.2 requires a separate assignment. 2. How many interlocks can be assigned to the P_Intlk function in PlantPax 3.2? - You can assign a total of 17 interlocks to the P_Intlk function in PlantPax 3.2. 3. Is it possible to transmit the Status interlock OK bit to a P_DOut block using P_Intlk in PlantPax 3.2? - Yes, you can transmit the Status interlock OK bit to a P_DOut block using the P_Intlk function in PlantPax 3.2. 4. Can I access all interlocks in a FactoryTalk View SE faceplate when using P_Intlk in PlantPax 3.2? - Yes, you can access all interlocks in a FactoryTalk View SE faceplate when utilizing the P_Intlk function in PlantPax 3.2.
Join hundreds of satisfied customers who have transformed their maintenance processes.
Sign up today and start optimizing your workflow.