I am currently seeking to integrate my PH meter data with the 1756-L81 using Rockwell's MODBUS AOI kit. I am unsure whether my PLC should be configured as a master or slave for MODBUS TCP communication. Are there any recommended strategies or considerations to keep in mind while using these AOIs? My ultimate goal is to solely import meter readings into the PLC without making any alterations to it.
While I have not personally worked with those AOIs, MODBUS operates using a Master/Slave architecture, which is similar to a Client/Server setup. The Master (or client) is the controlling entity that sends requests to the Slave (or server) device. In your situation, you should choose the Master role to request data from the PH Meter (the Slave). The setup process should be relatively simple from there. I recommend watching a helpful video tutorial on configuring Studio 5000 Modbus TCP Client for Allen Bradley Controllogix and Compactlogix systems.
In the realm of industrial automation, the PLC acts as the MasterClient while the field device operates as the SlaveServer. The traditional MasterSlave terminology has fallen out of favor for political reasons, with most vendors now adopting the ClientServer model. In this setup, the Client makes data requests, and the Server fulfills them. I have experimented with the use of AOIs on a few occasions. For small data requirements, it functions adequately. However, if dealing with numerous devices or extensive data, I would suggest investing in a specialized Modbus module. In my experience, placing it within a dedicated timed task of 50ms has proven effective.
LegacyLee mentioned a solution for the common "Overlap/Overload problem" in industrial automation - separating reads and writes into separate AOIs. While this approach can be useful for a small number of devices, it has its limitations. AOIs are memory-intensive and can be slow and non-deterministic due to their scripted nature. Despite these drawbacks, some users still find value in using the Modbus AOI.
I possess two devices, each containing a large amount of data points. While one device requires a one-second poll for temperature readings, the pH readings may take longer to process. Would it be advisable to execute two read AOIs and two write AOIs in this scenario?
If your data points are contiguous, you have the option to read and write them in a single transaction, with a maximum of 120 data points per transaction. The AOI supports 5 transactions, which will be executed sequentially one after the other. It typically requires 8 scans to complete a transaction. With a 50ms task, a transaction will take 400ms to finish, and with a 20ms task, it will take 160ms. The default polling rate is 1 second, but you can adjust it, considering the time it takes to execute a transaction. It is acceptable to use multiple AOIs on the Logix side, with each client AOI consuming one socket out of the 32 available. However, each AOI will establish its own TCP connection to the device. Keep in mind that some devices may restrict multiple TCP connections from the same IP address due to memory and processing limitations. Typically, devices permit either one TCP connection per IP address or only one TCP connection in total.
In your case, I would recommend configuring your PLC as a master in the MODBUS TCP communication, given that you're focusing on importing data from your PH meter into it. In this setup, the PH meter (a slave) will react based on the actions specified by the 1756-L81 (a master). Remember, when using Rockwell's MODBUS AOIs, timely data communication is crucial. Thus, consider the nature of your data: if it requires real-time acquisition, ensure your network can support such a high traffic demand. Lastly, a good practice is to sequentially request data from slaves when multiple slaves are involved, as this can prevent potential data congestion.
In terms of configuring your PLC for MODBUS TCP communication, it ultimately depends on the autonomy you want it to have. If you want your PLC to initiate the data request, then you should choose the master configuration. However, if you want your PLC to merely respond to requests, then the slave configuration might be more suitable. When using the MODBUS AOI kit, carefully map your inputs/outputs to ensure that data flows as expected. Be vigilant of your PH meter's data type and ensure compatibility for seamless integration.
In your case, it would be ideal to set the PLC as a master if you only intend to import data without making any changes to it. Masters initiate communication and typically garner data from slaves, fitting well with your requirements. Using AOIs can make the process smoother, but make sure to carefully configure each block according to your system's variables, and thoroughly test it before deploying. Consider allocating enough time for testing as troubleshooting may take longer when using AOIs. Remember that network conditions can heavily influence MODBUS TCP performance, so ensure you have a solid network setup.
Given the specific use case you've described, your PLC should ideally be set as a MODBUS TCP Master, which would allow it to request and receive data from your PH meter (acting as the slave). You should also account for the frequency of data requests, balancing between system load and the need for real-time readings. The AOI kit from Rockwell is well-documented, so don't hesitate to refer to the guides and examples provided. As you're only importing readings without any alterations, the setup should be fairly straightforward.
✅ Work Order Management
✅ Asset Tracking
✅ Preventive Maintenance
✅ Inspection Report
We have received your information. We will share Schedule Demo details on your Mail Id.
Answer: Answer: In this scenario, the Rockwell PLC should be configured as a MODBUS TCP master to communicate with the PH meter as a slave device.
Answer: Answer: It is essential to ensure proper configuration of the MODBUS communication settings, such as defining register mappings correctly and setting appropriate data types to accurately import meter readings into the PLC.
Answer: Answer: Yes, the MODBUS AOI kit can facilitate the integration of PH meter data into the Rockwell PLC without requiring any modifications to the PLC's existing programming or functionality.