Power Distribution Requirements for 1734-IT2I Module in Point IO System Installation

Question:

Considering the installation of a point io system, featuring a 1734-AENTR communications adapter along with ten 1734-IT2L modules. In the installation, a 1734-EP24DC module is added after every set of three IT2L modules. It may seem unnecessary to incorporate multiple EP24DC modules in this configuration. The 1734-IT2I module consumes 175mA, while the 1734-AENTR is capable of providing up to 1A of power (with a recommended maximum of 750mA) and the 1734-EP24DC can supply a maximum of 1.3A (with a recommended maximum of 1.0A).

Top Replies

I have encountered the limitation of only being able to use three 1734-IT2I modules per power supply. Additional modules can be added, but adding a fourth one often causes issues. While I have not found an explanation, it is clear that Rockwell is aware of this restriction as they do not allow configuration of more than three modules.

From a power perspective, incorporating multiple 1734-EP24DC modules actually makes sense in your configuration. Each 1734-IT2L module has a consumption of 175mA, so three would collectively consume 525mA power. If we take the 1734-AENTR's recommended maximum current of 750mA, after factoring in the three IT2L modules, you are left with just 225mA - which is borderline for buffering and system stability. Therefore, adding 1734-EP24DC after every set of three IT2L modules, with its ability to supply up to 1A power, gives you a more robust design and caters for any unexpected spikes in power consumption. Power considerations are crucial in any automation system design and it's better to safely exceed the needs than fall short.

Incorporating multiple 1734-EP24DC modules might seem like overkill at first glance, but it's actually a smart move. Given that each 1734-IT2I module consumes 175mA, having three underway quickly stacks up to 525mA. Add the consumption of the 1734-AENTR adapter into the mix, you'd easily be pushing the recommended upper limit. Inserting a 1734-EP24DC after every trio helps to distribute the power supply effectively, preventing any single module from getting overloaded. It provides a kind of reinforcing layer to your power distribution and ensures smoother operation. Think of it as a safety net for sustainable power management.

More Replies →

Streamline Your Asset Management
See How Oxmaint Works!!

✅   Work Order Management

✅   Asset Tracking

✅   Preventive Maintenance

✅   Inspection Report

We have received your information. We will share Schedule Demo details on your Mail Id.

To add a comment, please sign in or register if you haven't already..   

Frequently Asked Questions (FAQ)

FAQ: 1. What is the power consumption of the 1734-IT2I module in a point IO system installation?

Answer: - The 1734-IT2I module consumes 175mA of power.

FAQ: 2. How much power can the 1734-AENTR communications adapter provide in the point IO system?

Answer: - The 1734-AENTR communications adapter is capable of providing up to 1A of power, with a recommended maximum of 750mA.

FAQ: 3. What is the maximum power output of the 1734-EP24DC module in the point IO system installation?

Answer: - The 1734-EP24DC module can supply a maximum of 1.3A of power, with a recommended maximum of 1.0A.

FAQ: 4. Why are multiple 1734-EP24DC modules incorporated in the configuration with 1734-IT2L modules?

Answer: - It may seem unnecessary to incorporate multiple EP24DC modules in this configuration, as each IT2L module consumes 175mA and the EP24DC can provide more power than needed for each set of three IT2L modules.

FAQ: 5. What are the recommended power distribution requirements for the 1734-IT2I module in a point IO system installation?

Answer: - It is recommended to ensure that the power supply modules like 1734-AENTR and 1734-EP24DC can provide sufficient current to meet the needs of the IT2I module, considering