Hello, I'm curious if I can connect a 24vdc solenoid valve directly to a PLC output channel or if I should include a relay. Any guidance on this matter would be greatly appreciated. Thank you.
The decision on whether to use an interposing relay depends on the power consumption of your solenoid coil and the output rating of your IO module. Utilizing an interposing relay, particularly for controlling inductive loads, is often seen as a cost-effective precaution. Even if your output Amp rating surpasses the solenoid coil's amperage needs, installing a relay is a wise choice. It is more affordable and simpler to replace a relay than it is to replace an output module. This additional layer of protection can save you time and money in the long run.
When making a decision regarding solenoid control, it is crucial to have specific data on hand. Firstly, you should know the inrush and holding current of the solenoid. Secondly, you must ensure that the current rating of the PLC output module exceeds that of the solenoid. For larger solenoids, an interposing relay may be necessary. It is important to note that some PLC output modules share a common group of outputs and have limits on simultaneous usage. Consider the frequency at which the solenoid needs to be activated and deactivated, especially when using a contact output module. Transistor output modules typically have higher ratings for actuations compared to contact outputs due to their lack of moving parts.
To ensure proper functioning and avoid damage, it is crucial to follow these guidelines: Never connect anything other than an indicator light or a relay to a PLC output. It is recommended to use interposing relays for all devices controlled by a PLC. For instance, when installing a 16 output card, ensure to also incorporate 16 relays and sockets and allocate sufficient space in the panel. These small relays with bases are cost-effective at just $30 each, making them a practical alternative to replacing a faulty PLC card. Additionally, it is advisable to not directly wire field devices on machinery to a PLC input. Instead, route them through relays to provide clean control panel power to the PLC, reducing the risk of incorrect wiring that could potentially result in sending high voltage to a low voltage input terminal.
I_Automation strongly advises against wiring anything other than an indicator light or a relay to a PLC output to prevent damage. In a scenario where our output was driving a hydraulic solenoid within the output limits, frequent operation caused the output to fail within a couple of years. Implementing interposing relays on all outputs proved to be a cost-effective solution, saving the customer from purchasing another module. It is crucial to plan for the additional space required for relays when designing controls to ensure long-term reliability.
Looking for advice on wiring four solenoid valves to a single output channel of a PLC? The valves will operate simultaneously, each with a current of 15mA. Visit www.plctalk.net to join the discussion. Before proceeding, consider the rating and type of the output. Depending on factors like cost, frequency of operation, and whether it is solid-state or relay output, the feasibility of this setup may vary. Keep in mind the switching cycles and mechanical ratings of the output to make an informed decision. To ensure protection, consider using solenoid connectors with back EMF diodes and additional diodes and MOVs inside the box. Relays can also be a viable alternative for added security. Explore different perspectives before making a final decision.
Hi there! Generally, it's not recommended to connect a solenoid valve directly to a PLC output as the current draw of the valve may exceed what the PLC channel is rated for. Additionally, the PLC could get damaged from the back EMF generated when the solenoid is turned off. It would be safer and better for your system longevity to use a relay designed to handle the solenoid's current draw and voltage. Plus, it will help protect the PLC from potential damage. Remember to check the specifications of your solenoid and PLC to ensure compatibility.
Generally, it would be more advisable to use a relay. Directly connecting a 24vdc solenoid valve to the PLC output could possibly damage it due to the high inrush current of the solenoid. The relay acts as a buffer, protecting the PLC - a relatively expensive component - from any potential electrical surges. Be sure to select a relay with the proper coil voltage and contact rating to handle the current requirement of the solenoid valve.
It's great that you're exploring this! Generally, you can connect a 24V DC solenoid valve directly to the PLC output if the PLC output is rated to handle the load of the valve. However, it's often safer to use a relay, especially if the solenoid draws a significant current, since the relay will help protect the PLC from potential damage and give you some isolation. Just make sure to check the specifications of both your PLC and the solenoid to ensure compatibility!
It's great that you're diving into the details of your setup! Generally, it's safer to use a relay when connecting a 24VDC solenoid valve to a PLC output, especially if you're unsure about the current rating of the PLC output. Most PLCs can only handle a certain amount of current, and solenoids often draw more than that. A relay will help protect your PLC from unexpected loads and give you a more reliable operation. Plus, it allows for easier troubleshooting down the road!
✅ Work Order Management
✅ Asset Tracking
✅ Preventive Maintenance
✅ Inspection Report
We have received your information. We will share Schedule Demo details on your Mail Id.
Answer: Answer: Connecting a 24VDC solenoid valve directly to a PLC output channel is not recommended due to potential risks of damaging the PLC. It is usually advised to use a relay for proper isolation and protection.
Answer: Answer: Including a relay provides electrical isolation between the solenoid valve and the PLC output, helping to protect the PLC from voltage spikes and potential damage due to inductive loads.
Answer: Answer: Using a relay ensures proper voltage level matching, reduces the load on the PLC output, and enhances the overall safety and reliability of the control system.
Answer: Answer: Directly connecting a solenoid valve to a PLC output channel can lead to voltage spikes, interference, and potential damage to the PLC, which is why it is advisable to use a relay for better protection and control.