Troubleshooting 460-Volt Delta Transformer Issues: Seeking Insights on VFD Failures

Question:

Hello everyone, I recently began a new position at a well-established company located in Charlotte, NC. The electrical setup at the plant includes an aging 460-volt delta transformer system, which lacks a neutral or ground. After conducting some research, I've come across multiple sources indicating that newer Variable Frequency Drives (VFDs) can be problematic when connected to delta voltage systems. Unfortunately, I've experienced a loss of six PowerFlex drives within just two days—three 1 HP 40P models, two 3 HP 40P models in one system, and a 25 HP PFLX-70 in another, all for seemingly unknown reasons. To mitigate these issues, I am considering the installation of line reactors. However, I would greatly appreciate any insights or explanations regarding the potential causes of these failures. As someone who has never worked with a delta configuration before, I’m quite perplexed by this situation. Thank you in advance for any assistance you can provide! Best, Eli

Top Replies

As long as your supply voltage aligns with the drive's specifications, it should operate properly. It may also be beneficial to reach out to Rockwell for further assistance.

We have several older PF40 models in our inventory, and whether it's a sudden or scheduled power outage, it's almost certain that one or more of them will fail. It seems that earlier versions experienced problems with a specific component in the power supply. Did you recently experience a power interruption or fluctuation? If you don’t already have line reactors installed, adding them should be your top priority. It's a cost-effective safeguard for your equipment.

When assessing the supply transformers, it’s essential to check for any open circuits. A transformer winding may have failed, leading the system to mistakenly perceive a balanced three-phase supply despite one leg being imbalanced. I've encountered situations where line-start motors have burned out due to similar issues. For instance, I once dealt with a dual substation supplying a 7200V three-phase system that lost one of its power legs. The arrangement of the transformer banks compensated by generating a third phase, which fed back to the primary side, inadvertently powering motor loads on other circuits. This made troubleshooting quite difficult, as all voltage readings appeared normal (within acceptable limits) until we de-energized the substation transformers, at which point the actual problem became evident.

Based on my understanding, a delta power supply typically functions without any electronic faults—until an external load begins to draw power from it. Due to the absence of a grounding reference, the voltage levels can fluctuate significantly. This is where potential problems can arise. Grounding one of the phases introduces its own complexities; while you now have a solid ground reference, it may lead to one phase reaching a voltage significantly higher than expected, surpassing levels that would occur in a grounded wye supply. I’ve yet to delve into this topic in depth, but I've heard that delta supplies can potentially cause harmonics issues in drive applications. It's not that the delta configuration inherently produces harmonics; rather, it offers minimal dampening to mitigate them. However, I haven't thoroughly researched this to ascertain its accuracy. From my recollection, Allen-Bradley (AB) specifically favors center-grounded wye supplies as their optimal choice. Still, as others have pointed out, I have successfully operated drives on both grounded and ungrounded delta supplies without encountering any significant problems. Determining whether your situation is affected by the supply type can be challenging. Considering the known complications associated with delta supplies, I doubt that incorporating line reactors would be beneficial—unless the noise issue is more than just speculative. However, they are relatively inexpensive, so they won't hurt to try. Best regards, Keith

Have the MOV jumpers been removed from the malfunctioning drives?

Hey Eli, it sounds like you’re facing quite a challenge with that setup. Given that delta configurations can lead to voltage spikes and lack of grounding, those issues could definitely be contributing to the drive failures. Line reactors sound like a great solution to help mitigate inrush current and voltage transients that often come with VFDs in delta systems. You might also want to consider ensuring that your drives are properly rated for the configuration and maybe double-check any parameters related to over-voltage or insulation integrity. It could also be worth looking into the settings on the drives themselves, as sometimes minor tweaks can make a big difference. Good luck, and keep us posted on how things develop!

More Replies →

Streamline Your Asset Management
See How Oxmaint Works!!

✅   Work Order Management

✅   Asset Tracking

✅   Preventive Maintenance

✅   Inspection Report

We have received your information. We will share Schedule Demo details on your Mail Id.

You must be a registered user to add a comment. If you've already registered,
sign in. Otherwise, register and sign in.

Frequently Asked Questions (FAQ)

Ready to Simplify Maintenance?

Join hundreds of satisfied customers who have transformed their maintenance processes.
Sign up today and start optimizing your workflow.

Request Demo  →