I am dealing with a pre-existing project featuring IFM AL1222 IO blocks that are displaying an "EDS not registered" error. Despite successfully downloading the EDS using Rockwell's hardware installation tool, the project still shows the error and I am unable to see any IFM modules when adding a new module. I have tried opening the EDS tool as an administrator and closing out all RS Project and RSLinx Classic before using the tool, but the issue persists.
Additional information would be useful: Which version of RSlogix / Studio are you using? Have you installed the latest monthly patch from the Rockwell Automation website? Have you checked the device properties in RSlinx? The AL1222 functions as an IO-Link Master; have you downloaded the Ethernet/IP setup ZIP file from the IFM website? You may have already completed some of these steps.
Today, I encountered the same problem but found a solution in a forum thread. By shutting down all Rockwell Software and running the EDS Hardware Installation Tool as an Administrator, I was able to resolve the issue. Following these steps, I successfully identified all the newly added IFM EDS modules in my project.
Today, I encountered a similar issue but was able to resolve it by following a solution shared in a forum post. By closing all Rockwell Software and running the EDS Hardware Installation Tool as an Administrator, I successfully managed to detect all the newly added IFM EDS modules in my project. This workaround proved to be effective in solving the problem.
When working on my project, I encountered IFM AL1222 IO blocks with the issue of EDS not being registered. Despite using Rockwell's EDS hardware installation tool and successfully downloading it, the problem persisted in the project. I attempted various solutions such as running the EDS tool as an admin and closing out all RS projects and RSLinx Classic before searching for the module, but the issue remained. This has hindered my ability to add new IFM modules to the project.
To enhance your hardware installation process, run the installation wizard outside of the studio environment. This will give you the ability to manage and manipulate the installed eds files. It is common to encounter duplicates for a specific module, so be prepared for that. If you experience any issues, consider deleting all files from the ifm series, then redownload and reinstall to resolve the problem.
It sounds like a perplexing issue you're having. Have you checked if there are any version discrepancies between your RSLogix 5000 and the EDS of the IFM modules? Sometimes, even after a successful EDS download, version compatibility can come into play. You might need a specific version of RSLogix to successfully use the EDS. Also, consider uninstalling the EDS and reinstalling it, ensuring there are no software collision issues. I've faced a similar issue before, and it turned out that another software was causing a conflict. Another thing to note - after registering the EDS files, you might have to restart RSLogix 5000 or even your PC to see the changes. Best of luck in resolving this, keep us posted!
It sounds like you've covered most of the usual troubleshooting steps already. Have you tried resetting your PLC? Sometimes a simple reset can clear any pending tasks that may be interfering with the EDS registration. Consider also checking the compatibility between the versions of the EDS files and the RSLogix 5000 you are using. If none of these work, it might be a good idea to reach out to IFM or Rockwell directly for more advanced support. They might have come across this sort of issue before and could provide a more targeted solution.
It sounds really frustrating to deal with the "EDS not registered" error, especially after you've taken all the right steps! One thing you might try is double-checking the EDS files' location to ensure they’re in the right directory for Rockwell's systems to recognize them. It's also worth ensuring that the EDS version matches the firmware version of your IFM modules. Sometimes, clearing the RSLinx cache or re-registering the EDS files in the RSLinx Classic might help. If you haven’t already, checking the compatibility of your software versions can sometimes uncover hidden conflicts. Good luck!
It sounds like you've already taken some solid steps to resolve the "EDS not registered" issue. One thing you might want to double-check is whether the EDS files are correctly placed in the right directory for your RSLogix 5000 or Studio 5000 installation. Sometimes, the default installation can change, and if the files aren't in the expected path, they won't register properly. Additionally, make sure you've got the latest version of the EDS files for the AL1222 blocks, as older versions might not be compatible with your project. If the problem continues, consider clearing the EDS cache in RSLogix or looking into RSLinx Classic settings to ensure it's recognizing all the devices in your project.
✅ Work Order Management
✅ Asset Tracking
✅ Preventive Maintenance
✅ Inspection Report
We have received your information. We will share Schedule Demo details on your Mail Id.
Answer: Answer: Ensure that you have downloaded the EDS using Rockwell's hardware installation tool and try reopening the EDS tool as an administrator. Close out all RS Project and RSLinx Classic before using the tool to see if that resolves the issue.
Answer: Answer: The "EDS not registered" error may be causing this issue. Make sure the EDS is properly registered and try troubleshooting the error by following the steps mentioned in the thread content.
Answer: Answer: Yes, ensure that you download the EDS using Rockwell's hardware installation tool, open the EDS tool as an administrator, and close out all RS Project and RSLinx Classic before using the tool. These steps can help in troubleshooting and resolving the error.
Join hundreds of satisfied customers who have transformed their maintenance processes.
Sign up today and start optimizing your workflow.