Troubleshooting Gas Hot Plate with PID Control and Ball Valve Issues

Question:

Greetings, We are currently encountering an issue with a gas hot plate that is controlled by a PID system. The hot plate consists of six gas burners connected to a shared forced air manifold, with air flow and flame level regulated by a PID controlled ball valve. During the initial startup process, the ball valve is controlled by a PLC to manage the purge and ignition cycles successfully. Once all six burners are ignited, control is then transferred to the temperature controller. However, there are instances when the PID controller, set at a setpoint (SP) of 220 deg C and with a process value (PV) of 30 to 40 deg C, causes the ball valve to reduce the flame level below the desired limit. This results in the burners operating at a lower flame, slowly heating the hot plate to only 100 deg C, while the controller continues to adjust the ball valve to its minimum limit. To address this issue, the PID controller needs to be reset, the burners relit, and the controller can then resume normal operation by regulating the ball valve as intended. Despite changing the Controller, ball valve, and sensor Loop interface, the problem persists, indicating that the issue lies in the setup of the controller. The controller is currently in PI mode with specific parameters set, and the temperature sensor is located around 1.5 meters away from the flame. If anyone has any insights or advice on how to rectify this issue, it would be greatly appreciated. Warm regards, Ian

Top Replies

Could you provide more detail on whether the PI control is managed by separate dedicated controllers instead of being integrated within the PLC? If that's the case, how does the PLC adjust the controllers' output? I want to make sure I'm understanding the setup correctly.

parky inquired about the nature of PI control in relation to dedicated controllers and PLCs. Is the PI control conducted by separate controllers, or is it integrated within the PLC itself? During Purge and ignition processes, the PLC takes precedence over an external controller (such as a West 4170) by utilizing relays to bypass the controller's output. Following ignition, the external temperature controller resumes control as the PLC disengages the override relays. Observations have shown that the ball valve gradually adjusts to the Low Limit as the temperature controller outputs pulses. Ian provided this insight while on a job assignment, showcasing the intricate process of PLC and controller interactions.

Does the PID algorithm run continuously, even when control is taken over by the PLC? Do you observe the measured temperature exceeding the setpoint before any issues arise? Additionally, do you have access to information or data regarding the PID output?

Are you sure the controller is not set to adaptive tune or self-tune mode? Has this issue been present since the initial installation or has it recently appeared? It is not optimal to have a controller attempting to make adjustments while another process is interfering. This type of control is not typically seen, but when using standalone controllers, it is common to have a startup profile with incremental output adjustments. Check for these settings to ensure optimal performance.

ian.smith7 mentioned the transition of control from the PLC to the temperature controller when all 6 burners are ignited. This handoff can sometimes lead to complications. Can you elaborate on what is meant by "the PLC then releases control to the temperature controller?" Is the temperature controller referring to the PID system? Is the PID system set to automatic or manual mode before and after the PLC hands over control? How does the PID system handle changes in mode, such as transitioning from auto to manual? What are the setpoint (SP) and process variable (PV) values of the PID system before, during, and after the PLC releases control? For more insights, consider the concept of Rubber Duck Debugging.

Hi Ian, it sounds like a frustrating situation! One thing to consider is the positioning of your temperature sensor; being 1.5 meters away from the flame might be causing a lag in the readings, leading to the controller reacting too slowly. You might also want to look at tuning your PID parameters further—sometimes a bit of overshoot can help compensate for the delay in heating. If you haven’t already, experimenting with a feedforward control strategy in conjunction with the PID could improve responsiveness as well. Good luck, and I hope you get it sorted out soon!

Hi Ian, it sounds like you're dealing with quite a tricky situation! One thing you might want to consider is the placement of your temperature sensor; being 1.5 meters away from the flame could be causing delays in responding to actual temperature changes, contributing to the PID overshoot or undershoot. Additionally, have you tried tuning the PID parameters? Sometimes, relatively small adjustments in the integral or proportional gain can make a big difference in how the system reacts under varying load conditions. You might also want to check for any potential lag in the system due to the airflow dynamics that could affect the measurements. Good luck, and I hope you find a solution soon!

More Replies →

Streamline Your Asset Management
See How Oxmaint Works!!

✅   Work Order Management

✅   Asset Tracking

✅   Preventive Maintenance

✅   Inspection Report

We have received your information. We will share Schedule Demo details on your Mail Id.

To add a comment, please sign in or register if you haven't already..   

Frequently Asked Questions (FAQ)

FAQ: 1. Why is the PID controller causing the ball valve to reduce the flame level below the desired limit?

Answer: - The PID controller may be incorrectly configured, causing it to adjust the ball valve in a way that hinders reaching the desired temperature setpoint.

FAQ: 2. What troubleshooting steps have been taken to address the issue of the burners operating at a lower flame and slowly heating the hot plate?

Answer: - The thread mentions attempts to change the controller, ball valve, and sensor loop interface, indicating a systematic approach to resolving the issue.

FAQ: 3. What could be causing the persistent problem despite changing the controller, ball valve, and sensor loop interface?

Answer: - The issue may be related to the setup of the PID controller itself rather than the individual components, as indicated in the discussion.

FAQ: 4. What is the current mode of operation of the PID controller and the distance of the temperature sensor from the flame?

Answer: - The PID controller is in PI mode with specific parameters set, and the temperature sensor is located approximately 1.5 meters away from the flame, providing insight into the system configuration.