Troubleshooting GE 90-30 Power Warning Code 8402: Insufficient Power Usage Issue Detected

Question:

During application verification, a warning code 8402 may appear indicating insufficient power usage at 105.43% of the total system power supplied. This warning, located in Rack 0, Slot 0, could potentially cause system startup issues. If the system fails to start normally, there may be intermittent problems that require online interaction with the Programmable Logic Controller (PLC) and starting the process from Proficy. Any insights or solutions to resolve this issue would be greatly appreciated.

Top Replies

If your I/O module selection is causing the power supply to exceed its capacity, consider upgrading to a higher capacity power supply or redistributing modules to different baseplates. Occasionally, you may experience issues with the process not starting smoothly until you go online with the PLC and initiate it through Proficy. The software uses a conservative algorithm to estimate power consumption, so there may be instances where you can get by with the current module configuration. This could be the reason behind the intermittent issues. Additionally, review the PLC's fault tables for any indications of what might be causing it to stop.

Building upon Steve's insightful analysis, I would like to share one of my own experiences. When utilizing relay output modules, it is important to note that the coils for the relays on these modules consume more power compared to solid-state output modules. This factor becomes particularly significant if your application involves having most of the outputs activated simultaneously. However, for scenarios where only a few outputs are active at a time - such as in a central vacuum system where only one valve is open at any given moment - the power consumption may not be a major concern. It is crucial to conduct a thorough evaluation of your system to determine the best course of action. Despite being slightly over the recommended power threshold by just 5%, there is potential for optimization in your setup.

juhlik mentioned encountering a warning (8402: Insufficient power) while verifying their application. The warning indicated that the system was using 105.43% of the total system power supplied. Juhlik expressed concerns about this warning potentially causing issues with the system's normal startup process, leading to intermittent problems that require manual intervention with the PLC and Proficy to start the process.Thank you in advance for any insights provided. More details about your hardware configuration could help in providing further assistance. If your CPU has built-in Ethernet, low power might be the root cause of the intermittent startup issue.

I am transitioning from a GB controller to a PNS controller for an IO system. The system consists of 5 632 relays, 2 940 relays, and 1 650 relay. One of the 940 relays is not in use. It is possible for 2 to 4 of the other 940 relays to be activated simultaneously. Currently, with both 940 relays activated, I am at 168% capacity. If I deactivate one 940 relay, the capacity drops to 136%. The same 2 to 4 relays may be activated concurrently. Is this acceptable? The PNS controller consumes 1.1 Amps, which may be a concern.

Boost your device's performance with a more powerful power supply.

It seems like your system is drawing more power than what's being supplied, hence the 105.43% usage warning. This overdraw can often be because of some faulty hardware or software configurations. I recommend checking your equipment manufacturer's specifications to see if any components are exceeding the recommended power usage values. For the Proficy issue, restarting the process might help, but ensure that all your software patches and versions are up-to-date. Also, if possible, consider enhancing your power supply to your rack to avoid such issues in the future.

In my experience, a warning code 8402 usually suggests power supply issues. It's possible you might have too many devices drawing power from the same source, thus pushing the power usage to over 100%. Try redistributing the load or upgrade to a more powerful supply unit. If that doesn't solve it, fix any loose wiring because bad connections could cause this issue. Also, ensure to monitor the PLC status closely through Proficy while starting up the system to identify any intermittent errors during this process.

It seems like the system is drawing more power than it's designed to handle. This could be due to a faulty component or potentially a design flaw. In the short term, you might want to consider installing a more robust power supply unit if financially practical. For the long-term solution, it would be advisable to conduct a thorough inspection to find out why your system requires such a high power load. The inspection might reveal a faulty part that's demanding more power than it should, or a need for optimizing your code to make the system more energy-efficient. Also, don't forget to keep communication with your PLC uninterrupted and ensure the right process is followed in Proficy during startup to prevent potential issues.

It seems like your system is drawing more power than it can handle, which could be due to multiple reasons. One possible solution could be to check if any redundant components are running and consuming unnecessary power and shut them off. Moreover, you might need to optimize your system's operational performance to evenly distribute power. Also, ensure your PLC firmware is up-to-date - outdated firmware might not manage power effectively. In terms of initiating the process from Proficy, a firm understanding of the application's power needs should guide you in setting optimal parameters that don't exceed the system's total power supplied. Remember, it's crucial to resolve this issue to prevent overconsumption of power which might lead to system failure.

It sounds like you're dealing with a classic power supply issue that's affecting your system's startup. First, I’d check the power supply connections and ensure that everything is securely plugged in. Sometimes, just reseating the power connectors can resolve the problem. Additionally, consider whether any recent changes were made to the hardware that could have increased power demands. It might also be worth reviewing the power supply's specifications to confirm it meets the system's needs. If you have access to a power analyzer, running a diagnostic could pinpoint any irregularities. If the issue persists, consulting with your PLC documentation on error codes could provide specific troubleshooting steps tailored to your system.

It sounds like you're dealing with a tricky power issue! A warning code like 8402 often points to power supply instability, which can be pretty frustrating. Have you checked all the connections and ensured that your power supply is rated to handle peak loads? It might also help to look into any recent changes in your system configuration that could be affecting power distribution. If the issue persists, consider reaching out to your PLC support for guidance, as they might have specific troubleshooting steps or updates that can help stabilize your setup. Good luck!

It sounds like you're dealing with a tricky power management issue! First, make sure that all your power connections are secure and that your supply meets the system's requirements. It might also help to review the load distribution across the racks to see if any specific components are drawing more power than they should. If the warning persists, try resetting the PLC or checking the configuration settings in Proficy to ensure everything is optimized. Sometimes, a good firmware update can also resolve such glitches. Keep us posted on what works!

It sounds like you're dealing with a tricky power issue! First, I'd recommend checking all the power connections and ensuring that the system is receiving the correct voltage. It might also be helpful to look into the capacity of your power supply to see if it's actually able to meet the demands of your system, especially under load. If you continue to receive the 8402 warning, you could try resetting the PLC or updating any firmware to see if that resolves the anomaly. Additionally, running diagnostics through Proficy might give you more insights into any underlying problems. Good luck, and please keep us updated on what you find!

More Replies →

Streamline Your Asset Management
See How Oxmaint Works!!

āœ…   Work Order Management

āœ…   Asset Tracking

āœ…   Preventive Maintenance

āœ…   Inspection Report

We have received your information. We will share Schedule Demo details on your Mail Id.

To add a comment, please sign in or register if you haven't already..   

Frequently Asked Questions (FAQ)

FAQ: FAQs:

Answer: 1. What does warning code 8402 in a GE 90-30 system indicate? - Warning code 8402 indicates insufficient power usage at 105.43% of the total system power supplied.

FAQ: 2. Where is the warning code 8402 typically located in the system?

Answer: - The warning code 8402 is typically located in Rack 0, Slot 0 of the GE 90-30 system.

FAQ: 3. How can insufficient power usage affect system startup in a GE 90-30 system?

Answer: - Insufficient power usage, indicated by warning code 8402, can potentially cause system startup issues and lead to intermittent problems.

FAQ: 4. What steps can be taken to resolve the issue of insufficient power usage in a GE 90-30 system?

Answer: - If the system fails to start normally due to insufficient power usage, online interaction with the Programmable Logic Controller (PLC) and starting the process from Proficy may help resolve the issue.