My vendor provided me with a Micrologix 1400 PLC to replace my Allen Bradley Micrologix 1000. I am attempting to download the program using RS Logix 500 version 7.1, but I am encountering difficulties. I require assistance as I do not have access to an updated version of RS Logix 500.
Before making any changes, it is important to create a backup copy of your current RSLogix500 project file and keep it in a secure location to prevent accidental overwriting. In the project explorer window, locate and double-click on "Controller Properties". From the drop-down menu under "Processor Type", select the new controller type and click on "Apply". A prompt may appear asking to resize data tables, which should not cause any issues. The 1400 model has larger I/O image files compared to the 1000 series, so the program conversion should be successful. After making the necessary adjustments, verify the project and ensure no errors are detected at the bottom of the screen. If errors are found, they will need to be resolved manually as some instructions from the 1000 model may not be compatible with the 1400 model.
In order to successfully load the ML1400, it is required to have RSLogix 500 version 8.3 or higher.
In order to load the ML1400, you will need at least RSLogix 500 Ver 8.3. I initially thought that the ML1400 was supported in version 8.0, but upon further inspection, I realized the OP had 7.1. Remembering the specific version numbers required for hardware can be tricky, but Rockwell Automation's website likely has a helpful page for reference. Can anyone provide the link to save me from the tedious task of searching for it?
In a discussion thread, daba mentioned the compatibility of the ML1400 PLC in version 8.0 of the software, but noticed that the original poster was using version 7.1. Remembering the specific version numbers required for hardware can be challenging, but there are likely resources on Rockwell Automation's website to confirm this information. If anyone has a direct link to save time searching for this information, it would be greatly appreciated. Your assistance in sharing the link to download RS Logix 500 version 8.1 or higher for programming the ML1400 PLC is also requested.
It is recommended that you reach out to a nearby Rockwell distributor for assistance.
You may be encountering difficulties because the RS Logix 500, version 7.1 could well be incompatible with the newer Micrologix 1400 PLC. Keep in mind that the Micrologix 1400 is far more advanced, therefore it would generally require a more recent version of RS Logix 500. One potential solution would be to install an emulator to simulate the newer version, though this may not be optimal or feasible in every situation. Another option might be contacting your vendor for a possible software upgrade.
It sounds like you might be encountering compatibility issues with your current version of RS Logix 500 and the new Micrologix 1400 PLC. The version you're using may not fully support the features of the newer model. You may need a more updated version of RS Logix 500 to program the Micrologix 1400 properly. If you don't have access to the newer version, it might be worth consulting your vendor or reaching out to Allen Bradley's customer support for detailed troubleshooting guidance.
It seems like you might be dealing with software compatibility issues. The MicroLogix 1400 PLC is a bit more advanced than the MicroLogix 1000 and therefore might require a more updated version of RSLogix 500. Your vendor should provide you with the necessary software support. Meanwhile, you can try reaching out to Rockwell Automation - there's a possibility that they can guide you through a workaround or help you acquire a more recent version of RSLogix 500.
It sounds like you're running into a common issue since the Micrologix 1400 is not fully compatible with RSLogix 500 version 7.1, which was primarily designed for the Micrologix 1000 and earlier models. You might want to try using RSLogix 500 Starter if you can find a copy, as it supports both the 1000 and some 1400 models, or see if you can get a temporary license for RSLogix 500 8.0 or higher, which would definitely resolve any compatibility issues. If that's not an option, consider reaching out to your vendor for support; they may have some resources or suggestions for you as well!
✅ Work Order Management
✅ Asset Tracking
✅ Preventive Maintenance
✅ Inspection Report
We have received your information. We will share Schedule Demo details on your Mail Id.
Answer: Answer: Compatibility issues between the software version and the PLC model might be the root cause. Updating RS Logix 500 to a version that supports the Micrologix 1400 could resolve the problem.
Answer: Answer: While using the latest version is recommended for optimal compatibility and performance, it is possible to work with older versions by ensuring they support the specific PLC model being used.
Answer: Answer: You can contact Rockwell Automation for guidance on upgrading your software or explore online resources for downloading compatible versions of RS Logix 500. It is important to ensure the software is obtained from a legitimate source.
Join hundreds of satisfied customers who have transformed their maintenance processes.
Sign up today and start optimizing your workflow.