Troubleshooting Low Analog Input Values with SLC 500 and 1746-NI8 Card

Question:

I am currently investigating the possibility of a minimum threshold for analog input channels. Specifically, I am using a 1746-NI8 module with a SLC 500 programmable logic controller (PLC). It appears that my analog input leads may have been incorrectly connected, resulting in an input reading that is -25% of the expected range. Despite setting the analog input to 50%, the scaled value in the PLC shows -50%, indicating a possible issue with reversed leads. I am unsure if this discrepancy is related to a cutoff value not specified in the manual or if there are larger problems at play. With a looming deadline and limited time, I hope to troubleshoot and address any issues promptly to ensure the success of the project. Any advice or suggestions would be greatly valued as I work to resolve this issue efficiently.

Top Replies

The configuration of the channel is crucial, especially if it operates on a 4-20mA scale. In this case, a reading of 50% equates to 12mA, while -12mA (with reversed leads) could potentially be seen as 0mA due to a diode in the card for protection. On a 4-20mA scale, 0mA actually translates to -25%. Though not an expert on the workings of the 1746-NI8, the calculations seem to align correctly.

A decrease of 25% equates to 0mA, while a 0% reading corresponds to 4mA. It should be noted that the card does not register negative current; instead, it interprets it as no current, hence showing a -25% reading.

It indeed sounds like you've got a challenging issue on your hands! Based on your description, it seems likely that the issue could be arising from a hardware wiring error, considering you're seeing a -25% offset from the expected range. I'd suggest double-checking the wiring of your system thoroughly to ensure that there are no inverted or incorrectly connected leads. Also, check the configuration of the analog input in your PLC program. Make certain that the data scaling correctly corresponds to the voltage/current range of your sensor. It's surprising how many issues can be resolved by addressing these fundamental aspects. Let me know how it turns out!

It sounds like you're on the right track suspecting a reversed lead issue. This scenario can result in negative readings as you've observed. Before considering larger issues, first check for connection errors. Verify that your wiring corresponds properly to voltage/current configurations mentioned in the manual. After you're sure that the connections are correct and the problem persists, then it might be time to enter a deep dive into the module specifications. Remember, troubleshooting often involves iteration, so don't get discouraged, persistence will get you to the root of the problem.

It sounds like you're really deep into the troubleshooting process! Given the negative readings, I would definitely check the wiring connections first to confirm whether the leads are properly oriented. A common issue is that reversed connections can lead to unexpected values like you’re seeing, so double-check the pinout according to the manual. If that looks good, it might also be worthwhile to examine the scaling settings in your PLC to ensure they're configured correctly. Sometimes a simple recalibration can clear up discrepancies too. Good luck, and I hope you get everything sorted out before your deadline!

More Replies β†’

Streamline Your Asset Management
See How Oxmaint Works!!

βœ…   Work Order Management

βœ…   Asset Tracking

βœ…   Preventive Maintenance

βœ…   Inspection Report

We have received your information. We will share Schedule Demo details on your Mail Id.

To add a comment, please sign in or register if you haven't already..   

Frequently Asked Questions (FAQ)

FAQ: 1. How can I troubleshoot low analog input values with a SLC 500 and 1746-NI8 card?

Answer: Answer: To troubleshoot low analog input values, first ensure that the analog input leads are correctly connected. Check for possible issues such as reversed leads which can result in incorrect readings. Verify the scaling settings in the PLC to ensure they match the actual input values.

FAQ: 2. What could be causing the discrepancy between the expected range and the actual analog input readings?

Answer: Answer: The discrepancy between the expected range and the actual readings could be due to incorrect lead connections, incorrect scaling settings, or other issues with the analog input module or the PLC. It's important to carefully check all connections and settings to identify the root cause of the problem.

FAQ: 3. How can I address reversed leads affecting analog input readings in a SLC 500 system?

Answer: Answer: If reversed leads are affecting the analog input readings, ensure that the leads are connected correctly according to the wiring diagram provided in the manual. Reversing the leads can result in inverted readings, so correcting the connections should resolve this issue.