As a modbus master with the M340 (Schneider Electric) system, I have experienced smooth operation. However, when a disconnection occurs with the slave device, the system stops functioning even after the connection is restored. The only solution I have found is to restart the PLC. Is there a method to reset only the communication function without halting the PLC operations?
Share your code and access Schneider's reliable examples for working solutions.
To ensure proper function of the Read or Write function in the GEST array, it is crucial to set a nonzero timeout value beforehand. Failing to do so may result in the function never timing out, even if the GEST time is adjusted post-trigger. In such cases, a power cycle of the PLC is necessary.
Answer: 1. Q: What can be done when a disconnection occurs with the slave device in Modbus communication with M340 PLC? When a disconnection occurs, try resetting the communication function without halting the PLC operations by following specific procedures or utilizing certain features.
Answer: Explore methods to reset only the communication function without requiring a full PLC restart, ensuring smoother operation even after re-establishing the connection with the slave device.
Answer: Consider troubleshooting steps such as identifying potential causes of disconnections, checking configurations, and exploring ways to reset the communication function to resolve issues without stopping PLC operations.