I am struggling to establish a connection with my devices via Modbus. Although I have set the device ID, I am unsure of where to begin polling the registers. The documentation indicates starting at 2002, but a more accurate reading suggests starting at either 30000 or 40000. Have you had any experience with this issue? I am uncertain as to what I may be overlooking. Despite reaching out to customer support for assistance, they were unable to provide any help. The specifications for the device are as follows: 9600 baud rate, 8 data bits, no parity, and 1 stop bit. The device IDs are 81 and 82.
For those working with Modbus systems, it is essential to understand the various register numbering conventions used in the industry. One common notation is 5-digit reference notation, such as 32002 for Input Register 2002. Different Modbus vendors may use unique numbering schemes, so it is important to carefully review documentation to identify the correct registers. The VEGAFLEX 81 documentation specifically lists register 2002 as an Input Register, which is why the recommendation is to try using 32002 instead. Learn more about Modbus register numbering conventions in this informative post on control.com.
When troubleshooting Modbus register numbering issues, consider using the 5-digit reference notation 32002 for Input Register 2002, as recommended by Ijschulze. Various conventions exist for addressing Modbus registers within the industry. For more information on this topic, refer to the detailed discussion on Modbus Register Numbering. Different Modbus vendors utilize distinct notation methods in their documentation, making it essential to understand and differentiate between them. The VEGAFLEX 81 documentation specifies that register 2002 is an Input Register, hence the suggestion to try 32002. If you are experiencing issues with the MB Master Tank rung showing errors, further investigation may be necessary to address the issue.
Enhance the functionality of your functions by incorporating Tags into their STATUS outputs. By doing so, you can pinpoint potential errors through the error codes provided. Leveraging these STATUS outputs can prove to be invaluable for troubleshooting purposes.
It sounds like you're facing a bit of a puzzle with the Modbus setup! If the documentation mentions starting at 2002 but you're also seeing references to 30000 or 40000, it could be due to the different types of registers: 2002 may refer to a holding register, while 30000 and 40000 are usually associated with input registers. Make sure you're using the right function code for the type of register you're trying to read. Also, double-check if you need to adjust the offset; Modbus addresses can sometimes be 0-based or 1-based depending on the device. If you're still having trouble, using a Modbus simulator might help you verify your setup without the devices to ensure your communication parameters are correct. Good luck!
It sounds frustrating to deal with connection issues like that! In Modbus, register addresses can sometimes be a bit tricky, especially since different devices can map their registers differently. It might be worth checking if the device uses 0-based or 1-based addressing as that can affect where you should start polling. Usually, holding registers (40000 series) and input registers (30000 series) have different usage, so make sure you're trying to read the correct type. Also, double-check that youβre correctly setting the device ID in your requests. Sometimes doing a simple loopback test or checking with a Modbus tool can help debug where the issue lies. Keep at it; you'll get it sorted out!
β Work Order Management
β Asset Tracking
β Preventive Maintenance
β Inspection Report
We have received your information. We will share Schedule Demo details on your Mail Id.
Answer: - The documentation might suggest starting at address 2002, but more accurate readings indicate starting at either 30000 or 40000. It's advised to start polling at these addresses for the Vega Flex 81 device.
Answer: - The recommended communication settings are 9600 baud rate, 8 data bits, no parity, and 1 stop bit. Ensure that these settings are correctly configured in your setup to establish a successful connection.
Answer: - If you are facing difficulties despite setting the device IDs and communication parameters correctly, it's advisable to double-check the register polling addresses, verify the Modbus configuration, and ensure compatibility between the devices. Consider seeking further assistance or consulting additional resources for troubleshooting guidance.