Hello, I am encountering an issue with a PowerFlex755 drive as it constantly faults on a 'Net IO Timeout' every few seconds. My hardware setup is quite straightforward - I have created a test environment where my PC is connected to an ENBT card on my ControlLogix rack. The rack includes a GuardLogix processor with safety partner and another ENBT card directly linked to the drive, totaling 4 cards. I am able to successfully communicate with the drive using RSLinx, view live statistics, and have integrated it into my Logix5000 I/O tree. Despite matching drives and correlating parameters, the fault persists when the drive is in the rack and the program is running. Switching to program mode eliminates the issue, indicating a program-related fault. Additionally, when accessing the drive faceplate in the I/O tree and checking the 'connection' tab, the 'Module Fault' box displays '(Code 16#0203) Connection Timed Out' and repeatedly attempts to reconnect. Any guidance on troubleshooting steps and potential causes of this fault would be greatly appreciated. Thank you for your assistance. - Kane
After thorough investigation, I successfully resolved the issue at hand. The Ethernet/IP port embedded in the drive necessitates the Ethernet/IP scanner to utilize a suitable method for specifying quality of service (QoS). Unfortunately, the 1756-ENBT module I utilized did not meet the necessary firmware revision requirement (min 4.005), prompting me to conduct a FLASH upgrade. Subsequently, the problem was resolved. Additionally, it is important to ensure that if you are using a Stratix switch, the ports are configured to enable QoS.
We appreciate the follow-up, as it will undoubtedly benefit others in the future.
After encountering a persistent issue for 16 hours following the addition of new drives to a customer's system, I reached out to Tech Connect for assistance, spending three hours on the phone troubleshooting. After several unsuccessful web searches, I finally found the solution here. Thank you for posting - you saved me from a major headache.
✅ Work Order Management
✅ Asset Tracking
✅ Preventive Maintenance
✅ Inspection Report
We have received your information. We will share Schedule Demo details on your Mail Id.
Answer: Answer: The 'Net IO Timeout' fault on the PowerFlex755 drive could be caused by various factors such as network issues, misconfigured parameters, communication interruptions, or program-related faults.
Answer: Answer: To troubleshoot the 'Net IO Timeout' error, you can start by checking the network connections, verifying the parameters, ensuring proper communication settings, and analyzing the program logic for any faults that might be causing the issue.
Answer: Answer: The 'Net IO Timeout' fault may persist when the drive is in the rack and the program is running due to potential program-related faults or misconfigurations that are causing communication disruptions between the devices.
Answer: Answer: The 'Module Fault' box displaying '(Code 160203) Connection Timed Out' indicates that there is a timeout issue with the connection between the devices, which could be a result of communication failures or network interruptions.