Troubleshooting PowerFlex 753 Ethernet Connection Issue with 20-750-ENETR

Question:

Hello, I am currently experiencing an issue with my VFD. I am able to view the PowerFlex in Connected Components Workbench (CCW) and with RSLinx, I am able to establish a connection with CCW and everything appears to be functioning properly. However, when I try to upload the parameters using the Add-On Profile (AOP), the status in the tree only shows "Validating" and I am not seeing the PowerFlex status in the Tags. I am uncertain if the issue lies with the 20-750-ENETR, as I am able to connect with other software. My setup includes a 1756-L82E controller v32.11. I have attempted to resolve the issue by using a different version of the AOP, but the problem persists.

Top Replies

Encountering a corrupt configuration file is typically a clear indication of an issue. Have you copied the file from a different drive or created the instance from scratch? Have you utilized the offline match drive/synchronize feature to configure it? To resolve this, consider going offline, removing the drive, re-adding it, ensuring it matches offline, and then downloading the necessary program.

I appreciate your suggestion to toggle the unicast mode on and off again, and I can confirm that it has successfully resolved the issue. Thank you for your help with troubleshooting, it was extremely effective.

More Replies →

Streamline Your Asset Management
See How Oxmaint Works!!

✅   Work Order Management

✅   Asset Tracking

✅   Preventive Maintenance

✅   Inspection Report

We have received your information. We will share Schedule Demo details on your Mail Id.

To add a comment, please sign in or register if you haven't already..   

Frequently Asked Questions (FAQ)

FAQ: I am facing an issue with my PowerFlex VFD where the Add-On Profile (AOP) only shows "Validating" status when trying to upload parameters. What could be the problem?

Answer: The issue could potentially be related to the 20-750-ENETR module. It is recommended to troubleshoot the Ethernet connection between the VFD and the controller.

FAQ: I can establish a connection with Connected Components Workbench (CCW) and RSLinx for my PowerFlex VFD, but the parameters are not displaying correctly in the Tags. How can I resolve this issue?

Answer: It is advisable to check the compatibility and version of the Add-On Profile (AOP) being used. Trying different versions of the AOP may help in resolving the problem.

FAQ: My setup involves a 1756-L82E controller v32.11 with a PowerFlex VFD and 20-750-ENETR module. What steps should I take to troubleshoot the connectivity issue?

Answer: Ensure that the firmware versions of the controller, VFD, and Ethernet module are compatible. Additionally, verifying the network settings and configurations can help in troubleshooting the connectivity issue.