I'm currently installing a level sensor and facing challenges getting it to function properly. You can find the sensor details here: [Siemens Level Sensor Datasheet](https://cache.industry.siemens.com/dl/files/141/45351141/att_5659/v1/7ML19985KQ01.pdf). So far, I've connected +24V DC to terminal 1 and linked terminal 2 to the PLC input. However, when I submerge the sensor in water or another substance, the output signal remains unchanged—I consistently measure the same voltage between terminal 1 and terminal 2. The only observable change is the indicator light, which switches from green to red. What could be causing this issue? I noticed the datasheet mentions that the sensor is not suitable for low voltage PLC inputs. Does this mean it won't work at all with my setup? If so, why is that the case? Additionally, I came across a warning in the documentation stating: "The instrument must not be operated without an intermediately connected load, as this may damage the electronics if connected directly to the mains. It is not compatible with low voltage PLC inputs; it is intended for direct control of relays, contactors, solenoid valves, warning lights, horns, etc." It also says that when the load is switched off, the domestic current drops temporarily below 1 mA, ensuring that contactors requiring a lower holding current are reliably turned off. I appreciate any insights you can provide! Thank you!
We utilize this specific type for run-dry protection. "I consistently measure the same voltage between terminal 1 and terminal 2, but I've noticed the light changes from green to red." What is the accurate condition? Please refer to Figure 6.3. When the tuning forks come into contact with the medium, the switch deactivates, and the light indicator turns red.
The sensor's indicator lights operate as intended, serving as a high-level switch. In this configuration, when no product is present, the contact remains closed, while the contact opens in the presence of a product. However, I've observed that there is no variation in the input voltage whether a product is present or not. When the contact is closed, the voltage between terminals 1 and 2 should read 0 volts, as both terminals should match when the contact is closed. I'm puzzled as to why I’m measuring 14 volts even when the contact is closed. Is there an explanation for this voltage reading anomaly?
According to page 32 of the manual, the output circuit necessitates a minimum load of 10 mA to function effectively and can handle switching currents of up to 400 mA. In contrast, a standard 24 VDC PLC input draws less than 5 mA.
This device operates using a current of 3 mA. When the level switch is in the 'open' position, it actually allows 3 mA of current to pass through, which is sufficient for the PLC input to register the switch as being closed. It's important to note that this device is specifically designed for energizing solenoids rather than for direct use with PLC inputs. To adapt it for input use with a PLC, you will need to connect a resistor across the PLC input terminals. The resistor must have low resistance to ensure that the 3 mA current generates a voltage that remains below the activation threshold of your input card. Additionally, make sure the resistor can handle the wattage necessary to manage the current when the level switch closes, and 24V is applied to the resistor and input terminal.
Hey Steve, it seems we might be facing an issue. I’m planning to implement an interposing relay to resolve it. However, I’m struggling to understand this: I don’t notice any variation in the input voltage, whether or not there’s a product present. Additionally, when the contact is closed, the voltage measured between terminals 1 and 2 should ideally be 0V. Since it's just a closed contact, shouldn't the voltage be the same? I’m confused as to why I’m reading 14V when the contact is closed. Shouldn't the measurement between terminals 1 and 2 show 0V instead?
It sounds like you're on the right track with your connections, but the key issue here seems to be that this level sensor is designed to control high-power loads rather than work directly with low voltage PLC inputs. Since the datasheet states that it's not compatible with low voltage inputs, it likely means the output voltage from the sensor isn’t sufficient for your PLC to recognize a change. The fact that the indicator light changes gives you a signal that the sensor is functioning, but without an appropriate load connected (like a relay or contactor), it's not able to provide the proper output signal for your PLC. You might consider introducing an intermediary relay that can handle the sensor's output and then interface that relay with your PLC input. This way, you can ensure the sensor operates within its designed specifications while also making it compatible with your setup. Good luck with the installation!