Understanding Siemens CPU317-2Dp: Red BF2 Blinking and Red SF Lights - What Do They Mean?

Question:

I am in possession of a Siemens processor CPU317-2Dp showing a blinking red BF2 indicator and a consistently red SF indicator. I am unfamiliar with Siemens products and would appreciate any insights on the significance of these LED lights.

Top Replies

If you're seeing BF on your system, it typically signifies a bus fault or communication fault. Have you looked into your diagnostic buffer for more information? Providing a screenshot of the buffer could help us further assess the situation.

A more effective approach is to upload the complete diagnostics buffer to analyze the issue. You can easily download the diagnostics buffer as a text file by clicking on a designated button. The diagnostic report indicates a problem on interface X2 - the DP port, most likely due to difficulties in connecting to a configured Profibus DP slave. To resolve this, you should inspect for any shut down DP slaves, disconnected cables, damaged cables, or poor connector wiring. Be sure to address these potential issues to restore proper communication on the interface.

I identified an issue with one of the profibus stations where the connector was bent over. After replacing it, everything is functioning properly. Thank you for pointing me in the right direction.

I am in possession of a Siemens CPU317-2Dp processor displaying a flashing red BF2 led and a steady red SF led. I am unfamiliar with Siemens products and would appreciate any insights on the significance of these LED indicators.

I am encountering a flashing red BF2 LED and a steady red SF LED on my Siemens processor CPU317-2Dp. As someone with limited experience with Siemens devices, I am unable to interpret these LED indicators. Can anyone provide insight into what these lights signify?

Based on my experience with Siemens CPUs, a blinking red BF2 light could indicate a bus fault, possibly due to an issue with your Profibus connection. The solid red SF light is generally indicative of a system fault, which can range from minor configuration issues to serious hardware problems. I recommend checking your system diagnostic buffer for detailed error messages about the SF issue. You should also try to isolate and troubleshoot your Profibus segment to resolve the BF2 blinking problem. Of course, ensure everything is backed-up before you begin.

It sounds like you're dealing with a diagnostic issue. The blinking red BF2 light on a Siemens CPU317-2Dp generally indicates a bus fault, possibly due to some issue in communication. The consistently red SF means there's a system fault. Essentially, your processor is encountering some severe issues. I would suggest doing an overall system diagnostics to pinpoint the problem. Be sure to clear any minor faults before addressing the BF2 problem as even minor issues can sometimes cause a BF2 indication. Siemens also has quite comprehensive guides available online that detail all diagnostic light codes - they could provide some added insight.

It sounds like your Siemens processor is flagging a couple of issues. Usually, a flashing red BF2 LED indicates there's a problem with bus fault class 2, possibly a configuration error on the local bus you have. While the steady red SF (System Failure) LED denotes an issue is preventing the CPU from entering RUN mode. You might want to consider going through your system configuration or reach out to technical support for a detailed diagnosis.

More Replies →

Streamline Your Asset Management
See How Oxmaint Works!!

✅   Work Order Management

✅   Asset Tracking

✅   Preventive Maintenance

✅   Inspection Report

We have received your information. We will share Schedule Demo details on your Mail Id.

To add a comment, please sign in or register if you haven't already..   

Frequently Asked Questions (FAQ)

FAQ: FAQs:

Answer: 1. What does the blinking red BF2 indicator on a Siemens CPU317-2Dp signify? - The blinking red BF2 indicator on a Siemens CPU317-2Dp typically indicates a specific status or issue related to the processor. It is important to refer to the product manual or contact Siemens support for detailed information on the exact meaning of this LED indicator.

FAQ: 2. What does a consistently red SF indicator on a Siemens CPU317-2Dp indicate?

Answer: - A consistently red SF indicator on a Siemens CPU317-2Dp could signal a different status or problem. It is recommended to consult the user manual or reach out to Siemens technical support for clarification on the exact interpretation of the SF LED light.

FAQ: 3. How can I troubleshoot the red BF2 blinking and red SF lights on my Siemens CPU317-2Dp?

Answer: - To troubleshoot the red BF2 blinking and red SF lights on your Siemens CPU317-2Dp, you can start by checking the product manual for guidance on interpreting LED indicators. Additionally, you may consider performing system checks, verifying connections, and contacting Siemens support for further assistance in resolving any issues indicated by the LED lights.

Ready to Simplify Maintenance?

Join hundreds of satisfied customers who have transformed their maintenance processes.
Sign up today and start optimizing your workflow.

Request Demo  â†’